One is informed by the owner that two of the vessel's electrically driven centrifugal cooling water pumps will be replaced with two of higher capacity pumps. No modification of existing piping will be involved. What should be your concerns from an operational perspective?

AUpgrading of circuit breakers and controllers and possible increased erosion of discharge piping due to increased system velocities.
BPiping should be of no concern since it is designed with a safety factor. Electrical power should be of concern.
CElectrical power should be of no concern due to safety margins designed into power systems. Increased erosion may be a long term consideration.
DOne should not be concerned operationally since all systems are designed with future modifications/upgrades in mind.
AI Explanation

The correct answer is A) Upgrading of circuit breakers and controllers and possible increased erosion of discharge piping due to increased system velocities. The reasoning is that when replacing centrifugal cooling water pumps with higher capacity pumps, the increased flow rate can lead to higher system velocities in the discharge piping. This could result in increased erosion and wear over time, which should be a concern from an operational perspective. Additionally, the higher pump capacity may require upgrading of the electrical circuit breakers and controllers to handle the increased power draw, which is another important operational consideration. The other options are incorrect because B) and C) do not fully address the potential operational concerns with the increased flow rate, and D) is incorrect as operational considerations are important when making equipment changes, even if the systems are designed with future modifications in mind.

Want to practice with timed exams?

Download Coast Guard Exams for the full exam experience.

Get the App