Question 214Safety & Environmental - QMED

70% to pass

What would be the most probable cause for a high-pressure alarm to be activated in a low-pressure CO2 fixed fire extinguishing system?

AAn excessive amount of insulation has been installed on the tank and piping.
BAn air leak has developed in the tank.
CThe tank cooling system has malfunctioned.
DThe pilot cylinder discharge valve is leaking.
AI Explanation

The correct answer is C) The tank cooling system has malfunctioned. In a low-pressure CO2 fixed fire extinguishing system, the CO2 tank is kept at a low pressure, typically around 300-500 psi. This low pressure is maintained by a tank cooling system that keeps the tank at the proper temperature. If the tank cooling system malfunctions, the temperature of the CO2 in the tank will rise, causing the pressure to increase. This increase in pressure would trigger the high-pressure alarm. The other answer choices are incorrect because: A) Excessive insulation would not cause a high-pressure alarm, it would just make the tank harder to cool. B) An air leak would cause a low-pressure alarm, not a high-pressure alarm. D) A leaking pilot cylinder discharge valve would not directly affect the pressure in the main CO2 tank.