Question 176Refrigeration & AC - 1st Asst/Chief
70% to passIf a refrigeration compressor using a thermostat as a primary controller is running continuously without significantly lowering the temperature in the refrigerated space, which of the following is most likely the trouble?
The correct answer is D) a shortage of refrigerant. If a refrigeration compressor is running continuously without significantly lowering the temperature in the refrigerated space, it is most likely due to a shortage of refrigerant in the system. The refrigerant is responsible for absorbing heat from the refrigerated space and transferring it to the condenser. Without sufficient refrigerant, the compressor cannot effectively remove heat, leading to the continuous running without achieving the desired temperature. The other options are less likely to be the primary cause in this scenario. Excessive condenser cooling water (A) would not prevent the compressor from lowering the temperature. Warm food in the refrigerator (B) may contribute to the load, but would not prevent the compressor from functioning properly. A shortage of compressor oil (C) could cause issues, but would not necessarily result in the continuous running without temperature reduction.