Question 168Refrigeration & AC - 1st Asst/Chief

70% to pass

During tests to discover why a refrigeration compressor is running continuously, it is determined that the refrigerated space temperature is slightly above normal without ever reaching the desired minimum temperature. Suction and discharge pressures are normal for the corresponding box temperature. In this situation, what should you suspect?

Ahigh cooling water temperature
Ba shortage of refrigerant
Cleaking door gaskets
Dair in the system
AI Explanation

The correct answer is C) leaking door gaskets. Explanation: If the refrigerated space temperature is slightly above normal but never reaches the desired minimum temperature, and the suction and discharge pressures are normal, it suggests that the refrigeration system is operating correctly. In this scenario, the issue is likely due to heat infiltration from outside the refrigerated space, which would be caused by leaking door gaskets. Properly sealing the door gaskets is crucial to maintaining the desired temperature within the refrigerated space. The other options are incorrect because: A) high cooling water temperature would affect the discharge pressure, B) a shortage of refrigerant would cause low suction pressure, and D) air in the system would result in abnormal pressures.