Question 131Refrigeration & AC - Assistant Engineer

70% to pass

If a refrigeration compressor had developed a slightly high suction pressure accompanied with an abnormally low suction temperature, the problem could be a result of which of the following?

Aa clogged sub cooler
Ba leaking king valve
Cliquid refrigerant flooding back from the cooling coil
Da minor accumulation of air or non-condensable gases in the system
AI Explanation

The correct answer is C) liquid refrigerant flooding back from the cooling coil. If a refrigeration compressor has a slightly high suction pressure accompanied by an abnormally low suction temperature, it can indicate that liquid refrigerant is flooding back from the cooling coil. This can happen when the refrigerant charge is too high or the cooling load is too low, causing the refrigerant to not fully evaporate in the coil before reaching the compressor. The other options are incorrect because: A) a clogged sub cooler would cause high condensing pressure and temperature, not low suction temperature; B) a leaking king valve would cause low suction pressure, not high; and D) a minor air or non-condensable gas accumulation would cause high suction and discharge pressures, not the specific symptoms described.

Want to practice with timed exams?

Download Coast Guard Exams for the full exam experience.

Get the App