Question 368General Subjects - 1st Asst/Chief
70% to passAccording to 46 CFR regulations pertaining to tests and inspections as related to automatic auxiliary boilers, the fuel supply control solenoids must be checked for proper shutdown operation. What must be checked for?
AUpon a normal cycling or safety shutdown, the fuel control solenoid valve coil under test physically moves to the closed position.
BUpon a normal cycling or safety shutdown, voltage is removed from the fuel control solenoid valve coil under test.
CUpon a normal cycling or safety shutdown, voltage is applied to the fuel control solenoid valve coil under test.
DUpon a normal cycling or safety shutdown, the fuel control solenoid valve coil under test closes with no visible leakage into the burner(s).
AI Explanation
The correct answer is D) Upon a normal cycling or safety shutdown, the fuel control solenoid valve coil under test closes with no visible leakage into the burner(s). This is the correct answer because according to 46 CFR regulations, the fuel supply control solenoids must be checked to ensure that they properly shut off the fuel supply during a normal cycling or safety shutdown. Specifically, the regulations require that the solenoid valve physically closes and seals to prevent any leakage of fuel into the burner(s), which could create a safety hazard. Options A, B, and C do not fully address this key requirement of no visible leakage after the solenoid valve has closed.
Related Questions
Q396:Overhaul of a ship at a shipyard represents an example of a large-scale project ... Q311:When using a thermal imager for the purpose of conducting a thermo graphic analy... Q286:According to the Code of Federal Regulations Q33:Item "M" shown in the illustration is the _______________. Illustration MO-0110 ... Q251:Prior to entering the navigable waters of the United States after an internation...
Ready to test your knowledge?
Take a General Subjects - 1st Asst/Chief Practice ExamOfficial Resources