Question 245General Subjects - 1st Asst/Chief
70% to passWhile calibrating an electronic 4-20 mA or 3-15 PSI pneumatic controller, what is the value of 'Live Zero'?
A'0' for input span and another value for output range.
B4 mA or 3 PSI for process output range.
C'0' for span and range.
D4 mA or 3 PSI.
AI Explanation
The correct answer is D) 4 mA or 3 PSI. The 'live zero' for a 4-20 mA or 3-15 PSI pneumatic controller refers to the minimum value of the output range, which is 4 mA or 3 PSI respectively. This is the value that represents the zero or bottom end of the measurement or control range for the device. The live zero is not zero, but rather the lower end of the specified output range, which allows for detection of faults or issues with the system. The other options are incorrect because A) refers to the input span, not the output range, C) is incorrect as the live zero is not zero, and B) is partially correct but does not fully capture the definition of live zero.
Related Questions
Q347:In accordance with international MARPOL Annex V regulations and federal regulati... Q127:If you attempt to tighten a leaking hydraulic fitting with pressure on the syste... Q223:What temperature associated with the psychrometric properties of air is measured... Q65:Air leaking into a flash type distilling plant could occur through _____________... Q269:What statement is true when considering bunkering tank volume?