Question 305Electricity & Electronics - Assistant Engineer
70% to passUsing the temperature correction factor for the winding insulation temperature graph shown in the illustration, what would be the correction factor and the corrected temperature to 40 degrees C for a motor with an insulation resistance of 4 megohms measured at 50 degrees C? Illustration EL-0046

The correct answer is D) The temperature correction factor is 2 and the corrected resistance is 8 megohms at 40 degrees C. The reasoning is as follows: 1. Using the temperature correction factor graph for winding insulation resistance, a temperature change from 50 degrees C to 40 degrees C has a correction factor of approximately 2. 2. Since the insulation resistance is 4 megohms at 50 degrees C, applying the correction factor of 2 results in a corrected resistance of 8 megohms at 40 degrees C. The other options are incorrect because they do not accurately apply the temperature correction factor or calculate the corrected resistance based on the given information.
Ready to test your knowledge?
Take a Electricity & Electronics - Assistant Engineer Practice ExamWant to practice with timed exams?
Download Coast Guard Exams for the full exam experience.
Get the App